Minimum 12 V Power Supply for Screw Treminals

Post by craano » Fri Apr 10, 2020 7:48 pm

Hallo,
I got hands on a used Controllino Maxi. I am not sure if it is working.
Only the pins on top seem to be powered.
I cannot measure current with a multimeter on the screw terminals when switched to high.

How many amperes does the 12 volt transformer have to deliver to supply the screw terminals D0 ... D11 ?

Thanks.
craano

User avatar
Jarda
Posts: 45
Joined: Fri Dec 14, 2018 10:52 am

Re: Minimum 12 V Power Supply for Screw Treminals

Post by Jarda » Fri Apr 17, 2020 12:23 pm

Hello,
Do you have a load at outputs or are you connecting only the multimetr switched for current measurement ? ;-)

Each output D0..D11 has overcurrent protection and can deliver maximum of 2 A. You have to have proper load connected to there. And based on the load you have to select the proper 12 V power supply for CONTROLLINO. If you have some of the loads for example 5 A, than approx. 5,5 A power supply shall be selected.

Regards
Jarda

craano
Posts: 3
Joined: Fri Apr 10, 2020 7:17 pm

Re: Minimum 12 V Power Supply for Screw Treminals

Post by craano » Sun Apr 19, 2020 7:11 pm

Hallo,
i have only the multimeter switched to voltage measurement connected to the digital output and gnd.

So a power supply with 12V and 1A should be sufficient? But 0V is being displayed.
Thanks
craano

User avatar
Jarda
Posts: 45
Joined: Fri Dec 14, 2018 10:52 am

Re: Minimum 12 V Power Supply for Screw Treminals

Post by Jarda » Mon Apr 27, 2020 9:32 am

Hello,
yes, power supply 12V/1A shall be fine for this type of tests.

Do you have corresponding LED (D0-D11) on the TOP ON when you activate the output in your software?

Regards
Jaroslav

craano
Posts: 3
Joined: Fri Apr 10, 2020 7:17 pm

Re: Minimum 12 V Power Supply for Screw Treminals

Post by craano » Tue Apr 28, 2020 7:26 am

OK, thanks.
Just got a new controllino. Now all works fine and as expected.
The LEDs indicate if outputs are high/low and the voltmeter measures 12V/0V.
I Send back the used one. I think it is broken.
Thank you for your help.
craano

User avatar
Jarda
Posts: 45
Joined: Fri Dec 14, 2018 10:52 am

Re: Minimum 12 V Power Supply for Screw Treminals

Post by Jarda » Mon May 18, 2020 11:18 am

Hello,
thank you for information and I'm sorry for complication with broken CONTROLLINO.

Enjoy the new one.

BR
Jarda